ultrasonic detection of simulated corrosion in 1 inch diameter steel tieback rods
TRANSCRIPT
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
1/123
ULTRASONICDETECTIONOFSIMULATEDCORROSIONIN1INCH
DIAMETERSTEELTIEBACKRODS
By
KARLR.OLSEN
Adissertationsubmittedinpartialfulfillmentof
therequirementsforthedegreeof
DOCTOROFPHILOSOPHY
WASHINGTONSTATEUNIVERSITY
DepartmentofCivilandEnvironmentalEngineering
August2009
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
2/123
ii
TotheFacultyofWashingtonStateUniversity:
ThemembersoftheCommitteeappointedtoexaminethedissertationofKARLR.OLSENfindit
satisfactoryandrecommendthatitbeaccepted.
DavidPollock, Ph.D.(Chair)
DavidMcLean, Ph.D.
DonaldBender, Ph.D.
William Cofer, Ph.D.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
3/123
iii
Acknowledgements
"Forbyhimallthingswerecreated:thingsinheavenandonearth,visibleandinvisible,
whetherthronesorpowersorrulersorauthorities;allthingswerecreatedbyhimandforhim."
Colossians1:16
FirstandforemostIwouldliketothankmyparents. Dad,withoutyourencouragementtosee
beyondmytrialsIwouldhavegivenuplongago. Iconsideritanhonortohaveyouasafather,
amentorandafriend. Mom,thankyouyourunwaveringlove,regardlessofmy
accomplishmentsorfailures. Iamproudtobeyoursonandthankfulforeverysmileandhug
thatawaitsmeeverytimeIseeyou.
Dr.Pollock,IhavelearnedasmuchfromwatchingyouasIhavefromlisteningtoyour
feedback. Yourcareforyourstudentsaboveyourselfisevident,andaninspiration. Toall
thosethathelpedkeepmesanethroughoutthisprocessandremindmethatthereismoreto
lifethanadissertation: Alan,Neil,Mike,Chuck,Jacob,Rebekah,Jessie,Laura,andKristinayour
friendshipmeansmorethanyouknow.
Also,thisdissertationwouldnothavebeenpossiblewithoutfundingforthisproject,whichwas
providedbytheU.S.DepartmentofTransportation(USDOT),TransportationNorthwest
(TransNow)RegionalResearchCenterthroughcontractnumber430820. Thecommercialall
threadtiebackrodswereprovidedbyWilliamsFormEngineeringCorporation.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
4/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
5/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
6/123
vi
Contents
1 IntroductionandObjectives.................................................................................................... 1
1.1 TiebackRods..................................................................................................................... 1
1.2 ProblemStatement.......................................................................................................... 2
1.3 ResearchObjectives......................................................................................................... 3
1.3.1 DetectPhysicalGeometryofSimulatedCorrosioninSteelRods.............................3
1.3.2 EvaluateThreadedWilliamsTiebackRods............................................................... 4
1.4 OutlineofDissertationContents..................................................................................... 4
2 BackgroundandLiteratureReview......................................................................................... 6
2.1 PressureWaveProperties................................................................................................ 6
2.2 TwomethodsforSolvingtheWaveEquation.................................................................. 8
2.3 BackgroundinUltrasonicWavesinRods....................................................................... 13
2.3.1 UltrasonicWave...................................................................................................... 14
2.4 UltrasonicApplications.................................................................................................. 17
2.4.1 PreviousUltrasonicResearch................................................................................. 17
3 ExperimentalSetupandTesting............................................................................................ 22
3.1 ExperimentalSetup........................................................................................................ 22
3.2 LabviewProgram............................................................................................................ 23
3.3 TransducerCharacterizationandSelection................................................................... 23
3.4 WavelengthinSteelRod................................................................................................ 26
3.5 EndPreparationandTransducerCoupling.................................................................... 27
3.6 SteelRodsUsedinTesting............................................................................................. 28
3.7 VelocityCalculationforSteelRods................................................................................ 29
4 DetectingPhysicalGeometryofSimulatedCorrosion..........................................................33
4.1 LocationofLeadingEdgeofSimulatedCorrosion.........................................................33
4.2 DiameterCharacterization............................................................................................. 36
4.3 LengthofSimulatedCorrosionCharacterization...........................................................45
4.3.1 ChangeinFrequencyContentofBackEchoforLengthofSimulatedCorrosion...46
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
7/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
8/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
9/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
10/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
11/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
12/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
13/123
1
1 IntroductionandObjectivesIn2002,justeastofdowntownCleveland,Ohio,severaltiebackrodsinasheetpileearth
retainingwallfailed(Esser&Dingeldein,2007). Thefailurewasduetocorrosionandcauseda
nearcollapseofthewall. Corrosioninstructuralsteeltiebackrodscausesadecreaseincross
sectionalarea,limitingtensileloadcapacity. Tiebackrodsaretypicallyburiedinsoil,
eliminatingtheoptionofvisualinspectionwithoutexcavation. Theresearchinthisstudy
evaluatedultrasonictestingasamethodofdetectingsimulatedcorrosioninsteelrods.
1.1 TiebackRodsTiebackrodsareavitalcomponentofsheetpile retainingwalls. Therodsconnecttheouter
supportstructuretoanchors(ordeadman)buriedinthesoil(Figure1.) Thefirsttiebackrods
Figure1. Sheetpileearthretentionwalls(USArmyCorpsofEngineers,1994)
Wale
SheetPiling
Wale TieRod
TieRodConcrete
Deadman
SheetPiling
Anchor
SheetPiling
a.Tierodsanddeadman
b.Tierodsandanchorwall
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
14/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
15/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
16/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
17/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
18/123
6
2 BackgroundandLiteratureReviewThischapterpresentsabackgroundofultrasonicwaves. Anoverviewoffundamentalwave
propagationprovidesthebasisforunderstandingultrasonicwaves. Theuseofultrasonic
wavesinnondestructivetesting(NDT)ispresented,includingpreviousresearchpertaining
specificallytosteelrods.
2.1 PressureWavePropertiesAwaveisadisturbancethatpropagatesthroughtimeandspace. Energyistransferredfrom
onepointtoanotherviawaves. Asinglefrequencybulkwaveischaracterizedmathematically
bythewavelength()andamplitude(A)ofthesignal(Figure2). Thewavelengthisthedistance
betweentwoadjacentpeaksinthewavecycleandtheamplitudeisthemaximumdisplacement
ofthedisturbancefromtheundisturbedposition. Thefrequency(f)ofthewaveisdefinedas
Figure2. Mathematical wavecharacterization
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
19/123
7
thenumberofoscillationsthatoccurinonesecondandtheperiod(T)isthetimetocomplete
oneoscillation.
Phase
Velocity
Thespeedatwhichthebulkwavetravelsthoughamediumiscalledthephasevelocity(p)and
iscalculatedwiththefollowingequation(Main,1988).
Equation1Thephasevelocityisdependentuponthetypeofwavetravelinginthemedium. Longitudinal
andshearwaveswillbeconsideredinthisresearch. Longitudinalwavesexhibitparticlemotion
inthedirectionofwavepropagation. Shearwavesexhibitparticlemotionorthogonaltothe
directionofwavepropagation.
Snell'sLaw
Whenalongitudinalwaveencountersaboundarysurface,longitudinalandshearwavesare
reflectedbackintothemediumatanglesdeterminedbySnell'sLaw(Figure3). Theresulting
longitudinalwavereflectsatanangleequaltotheincidentangle. Thereflectedshearwavehas
1
2
1
Figure3. DiagramofSnell'sLaw
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
20/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
21/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
22/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
23/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
24/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
25/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
26/123
14
willestablishthetheoreticalfoundationthatwillbebuiltupontocompileamorecomplete
understandingofultrasonicwavesinrods.
2.3.1 UltrasonicWaveUltrasonicwavescanbeinitiatedinsteelrodsusingapiezoelectrictransducer. Anelectric
signalwassenttothetransducerconvertingelectricalenergytomechanicalenergyintheform
ofapressurewave. Whencoupledtotheendofasteelrodthewaveisgeneratedinthesteel
rodandproceedstotravelthelengthoftherod. Atthispointareceivingtransducercandetect
thesignalattheotherendoftherod,oriftheendoftherodisnotaccessible,thewave
reflectsfromtheendsurfaceoftherodandtravelsbacktothetransducer. Asthewave
returnstothefrontend,thetransducerconvertsthemechanicalenergyintoelectricalenergy,
andtheelectricalsignalisrecordedbythecomputer. Theultrasonicsignalforastraightrod
withoutanyflawsisshownbelow(Figure6).Themainbangrepresentsthegenerationofthe
ultrasonicwave. Thesmallsignalfollowingthemainbangisaringingoutofthepiezoelectric
transducer. Thenextsignalthatappearsisthefirstbackecho,whichrepresentsthefrontof
Figure6. Standardultrasonicsignalfrom1.0ft.long1.0in.diametercircularrod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
27/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
28/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
29/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
30/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
31/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
32/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
33/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
34/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
35/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
36/123
24
inspections. Themainvariablesincommercialtransducersarethediameterofthetransducer
andthefrequencyoftheultrasonicsignalgenerated. Thefollowingisalistoftransducers
availablefortestingofthesteelrodsinthisresearch(Table1.) Usinga1.0in.diameterrod
threefeetlongwithnoflaws,themaximumamplitudeofthebackechoforeachtransducer
wasrecorded(Figure15.) Thedatashowsthatthe5MHztransducerswith0.5in.diameter
providedthelargestamplitude. Transducerswhichproducelargeechoamplitudeswill
Figure15. Transduceramplitudecomparisononarodwithnosimulatedcorrosion
increasethemaximumdetectablelengthofrod. Thetransducerswerealsotestedtomake
suretheycandetectareductionindiameterfrom1.0in.to0.75inlocated2in.alonga6in.
longrodwitha1in.diameter. Thesignalresponsewasmeasuredtofindthemaximum
amplitudeoftheflawechoandbackecho(Figure16). The0.5in.diameter5MHz
transducersprovidedthemaximumflawechoandbackechoamplitudesata40dBgainsetting
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
37/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
38/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
39/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
40/123
28
wasappliedbeforethetransducerwascoupledtotheendoftherod. Withoutthegel,the
transducercouldnoteffectivelycoupletheultrasonicsignalintotherod,resultinginan
extremelypoorultrasonicwave,ifanyatall. Amagnetictransducerwasusedinmostteststo
provideaconsistentadheringforcebetweenthetransducerandtheendoftherod.
3.6 SteelRodsUsedinTestingTwotypesofsteelrodswereusedinthisresearch(Figure18). 12L14steelrodswereusedfor
fabricatingandtestingvariousgeometriesofsimulatedcorrosion. Williams75ksiallthread
tiebackrodswereusedtoconfirmdetectionofultrasonicwavesinactualtiebackrods. The
propertiesofthe12L14steelandWilliamsgrade75steelareshowninTable2.
Williams tieback rod 12L14 cold drawn rod stock
Figure18. Williamscommercialtiebackrodand12L14rodstockusedintesting
12L14Steel
Thesimulatedcorrosiongeometriesweremachinedfrom1in.diametercoldrolled12L14steel.
12L14isaleadbasedsteelwithasmoothsurfacethatisidealformachining. Thesteeliscold
drawnandfabricatedaccordingtoASTMA108(ASTMStandardA108,2007)orASTMA29
(ASTMStandardA29,2005).
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
41/123
29
WilliamsGrade75AllThreadTiebackRods
Williams1in.diametertiebackrodswereusedtoevaluatethedetectionofultrasonicwavesin
commercialrods. Thegrade75allthreadrodswereacontinuouslythreadedrodspecially
designedtobeusedasconcreteformingtierodsandanchors. Allthreadtiebackrodsare
availableinlengthsupto50feet.Therodsaremanufacturedwithaspecialthreaddesignedto
meettherequirementsofASTMA615(ASTMStandardA615,2008).
Table2.Propertiesfor12L14steelandWilliamsgrade75tiebackrod
Property 12L14 Williams tieback rod
Density (lbs/ft3) 481 - 501 481 - 501
Poisson's Ratio 0.27 - 0.30 0.27 - 0.30
Elastic Modulus (ksi) 27,560 - 30,460 27,560 - 30,460
Tensile Strength (ksi) 78 100
Yield Strength (ksi) 60 75
3.7 VelocityCalculationforSteelRods
Determiningthewavespeedinthesteelspecimenswasnecessaryforcalculatingspecific
geometriesofthesteel. Ultrasonicsignalswererecordedfor1.0ft.longsectionsof12L14steel
andgrade75Williamstiebackrods. Itwasnecessarytodeterminethewavespeedusingthe
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
42/123
30
firstandsecondbackecho. Apotentialdelayinthesignalcanoccuratthemainbang,because
thesignalismeasuredastheelectricalimpulseentersthetransducer,butthebackechoesare
measuredwhentheultrasonicwaveimpactsthetransducer. Afullsignal,containingtwoback
Figure19.Fullultrasonicsignalfor1.0ft.long1.0in.diameter12L14steelrodforcalculatingwavespeed
echoeswasrecorded(Figure19).Todeterminethearrivaltimeofthebackecho,itwas
necessarytodeterminewhenthebackechosignalfirstrisesabovethenoise. Thegraphsofthe
firstandsecondbackechoesareshownbelowtodeterminethestarttimeofeachbackecho
(Figure20.) Tofindthestarttime,itwasfirstnecessarytoinspectthemainbangsignal. The
directionthatthesignalamplitudefirsttravelsaboveorbelowthehorizontaltimeaxis
determinesthedirectionofthearrivalofthebackechoes. Inthecaseshown,themainbang
travelsinthenegativedirectionfirst;thusthearrivalofthefirstandsecondbackechoeswill
occurinthenegativedirection. Individualpointswereplottedinthegraphstovisualizethe
departureoftheechoesfromthesignalnoise.Thearrivaltimesofthemainbangandfirstand
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
43/123
31
Figure20. Mainbangandfirstandsecondbackechoesfor1.0ft.long1.0in.diametersteelrod
secondbackechoeswererecorded(Table3). Then,thetimebetweenthefirstandsecondback
echoeswasdividedbytwotofindthewavespeedperfootofrod. Twolengthsarenecessary
toaccountforthewavetravelingdowntherodandthenreturningtothetransducer. Thebulk
longitudinalwavespeedsforthesteelusedinthefollowingresearchareshownbelow(Table
4.) The12L14SteelusedforthesimulatedcorrosionrodsandtheWilliamstiebackrods
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
44/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
45/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
46/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
47/123
35
Figure24.Ultrasonicsignalsforsimulatedcorrosionlocatedat8.94in.,16.06in.,and23.03in.fromtheendof
therod.
Thelength,L,fromthetransducertotheleadingedgeofsimulatedcorrosioncanbecalculated
usingthefollowingformula:
Equation27
whereC1isthebulklongitudinalwavespeedofthematerial,andtisthetimebetweenthe
mainbangandtheleadingedgeoftheflawecho. Thetimewasdividedbytwobecausethe
ultrasonicpulsepassesdownthelengthoftherodtotheflawandthenreturnsbacktothe
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
48/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
49/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
50/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
51/123
39
Thesecondsetofrodsincludeda3ft.long1.0in.diameterrodwitha2.0in.lengthof0.5in.
diametersimulatedcorrosion,a3ft.long0.5in.diameterrodwithoutsimulatedcorrosionand
a3ft.long1.0in.diameterrodwithoutsimulatedcorrosion(Figure28). A45transitionwas
includedateachendofthesimulatedcorrosiontoaddresstheconcernthatcorrodedregions
donottypicallyexhibitanabrupttransition. The45transitionalsoreducedtheamplitudeof
thesecondflawechothatoccuredcoincidentwiththebackechointheultrasonicsignal. These
rodswereusedtoinvestigatetheeffectof0.5in.diametersimulatedcorrosiononthe
ultrasonicsignal. Thebackechoandsuccessivetrailingechoeswererecordedforeachrod
(Figure29). Thetimebetweenthetrailingechoes(t)foreachofthethreerodswasrecorded
3ft.
0.50 in.
36in.
1.00in.
Figure28. 1.0in.diameterrodwith 0.5in.simulatedcorrosiondiametercomparedwith0.5in.diameter and
1.0in.diameterrods
*Transducerwasmounted
onleftendoftherod.
*Thetransitionindiameterwas45asshown
atright
45
16.0625in.
3ft.
0.500 in. 1.00 in.
2.0 in.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
52/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
53/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
54/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
55/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
56/123
44
outerdiameterisamultipleofthesimulatedcorrosiondiameterthesuperimposedtrailing
echoesarriveatthesametimeappearingasasingletrailingechoes. Thetimebetweentrailing
Table8. Calculateddiameterfor1.0in.diameterrodwith0.5in.and0.75in.diametersimulatedcorrosion
Specimen
Smallest
Diameter (in.)
Measured
t(s)
Calculated
Diameter(in)
%
Difference
0.5in.Simulated
CorrosionDiameter0.5 3.50 0.53 6.6%
0.75in.Simulated
CorrosionDiameter0.75 4.76 0.73 3.2%
echoeswasmeasuredandthecorrespondingsimulatedcorrosiondiameterwascalculatedas
0.53in. Theseresultsshowedthat0.5in.diameterand0.75in.diametersimulatedcorrosion
canbecalculatedin1.0in.diameterrodsusingEquation25. Thetimebetweentrailingechoes
mustbemeasuredfromthebackechotothefirsttrailingechotodetectthesmallestreduced
Figure32. Percentreductionoforiginalloadcapacityforsimulatedcorrosionina1in.diameterrod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
57/123
45
diameter. Thereductionindiameterofasteelrodcorrelatesdirectlywithareductionofload
capacity. Thetensileloadcapacityofasteelrodisdependentuponthesmallestcrosssectional
areaoftherodperpendiculartothelongitudinalaxis. Thereductioncanbecalculatedin
percentoforiginalloadcapacitybasedupontheoriginaldiameter(do)andthecorroded
diameter(dc). Thepercentreductioninloadcapacityfora1in.diameterrodwithreduced
crosssectionisplottedinFigure32. The0.75in.diametersimulatedcorrosionrepresentsa
43.75%reductioninloadcapacityandthe0.5in.diameterrepresentsa75%reductioninload
capacity.
% Equation28
4.3 LengthofSimulatedCorrosionCharacterizationInordertoinvestigatetheeffectoflengthofsimulatedcorrosionontheultrasonicsignalthe
backechoandfirsttrailingechowereexamined. Thefrequencycontentofthebackechowas
inspectedforashiftofthepeakfrequencywithachangeinthelengthofsimulatedcorrosion.
Also,theratioofmaximumamplitudesofthetrailingandbackechoeswereexaminedfora
changewiththelengthofsimulatedcorrosion. Allultrasonicsignalspresentedinthissection
weregeneratedwiththeM1042OlympusNDT5MHztransducer.Thesignalwaveformand
frequencycontentareshowninFigure33.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
58/123
46
Figure33. Signalwaveformandfrequencycontentfor5MHzM1041OlympusNDTtransducer
4.3.1 ChangeinFrequencyContentofBackEchoforLengthofSimulatedCorrosionThefrequencycontentofthebackechowasinvestigatedtoidentifyanytrendsassociatedwith
thelengthofsimulatedcorrosion.Thebackechoesofseveralrodswithvariouslengthof
simulatedcorrosionwereevaluatedusingaFastFourierTransform(FFT). TheFFTanalysisof
thebackechoshowsthefrequencycontentofthetimedomainsignal. AnFFTrequiresthe
numberofdatapointsbe2NwhereNisaninteger. Todecreasetheeffectofnoiseonthe
signalonlytheoscillationswhichcrossthexaxiswereconsideredintheanalysis,andthe
remainderofthesignalwasreplacedwithzeros(Figure34.) Beforethefrequencyofthesignal
wasanalyzedforsimulatedcorrosion,twotestswereperformedtoinvestigatetheeffectof
lengthanddiameteroftherodonthefrequencyoftheultrasonicsignal. Thefirsttestincluded
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
59/123
47
Figure34. Backechoof1.0ft.longrodwitha0.5in.simulatedcorrosiondiameterwithandwithoutzeros
threerods3.0ft.inlengthwithdiametersof0.5in.,1.0in.,and1.5in. AnFFTwascalculated
forthebackechoineachrod. Thepeakfrequenciesforthe0.5in.,1.0in.,and1.5in.diameter
rodswere6.10MHz,3.91MHz,and4.39MHzrespectively(Figure35). Thesecondtest
includedthreerods1.0in.indiameterwithlengthsof1.0ft.,3.0ft.,and10.0ft. AnFFTwas
calculatedforthebackechoineachrod. Theresultsshowedthatthepeakfrequenciesforthe
1.0ft.,3.0ft.,and10.0ft.longrodswere4.39MHz,3.66MHz,and4.64MHz(Figure36.)
Figure35andFigure36showthatthepeakfrequencyofthebackechocanvarywithbothrod
diameterandrodlength. However,adefiniterelationshipbetweenpeakfrequency,rod
diameterandrodlengthwasnotestablishedinthisstudy.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
60/123
48
Figure35. FFTfor3.0ft.longrodswith0.5in.,1.0in.,and1.5in.diameters
Figure36. FFTforbackechoof1.0in.diameterrodswith1.0ft.,3.0ft.,and10.0ft.lengths
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
61/123
49
Twosetsofrods1.0in.indiameterand1.0ft.and3.0ft.inlengthweretestedtoidentifyany
correlationforeachspecificlengthanddiameterofrods. Thefirstsetofrodsincludedfive1.0
ft.longsteelrodswith0.5in.simulatedcorrosiondiameterforlengthsof0.5in.,1in.,2in.,4
in.,and8in.(Figure37). A90transition,fromtheoriginalroddiametertothesimulated
corrosiondiameter,wasusedoneachrod. Thelocationofthesimulatedcorrosionwas2.0in.
fromtheendofeachrod. TheFFTforthebackechowascomparedforeachofthefiverods
Figure37. 1.0in.diameter1.0ft.longrodswithdifferentlengthsofsimulatedcorrosion
8in.
12in.0.500
1.00
2.0in.
9in.
12in.0.500
1.0
1.00
9.5in.
12in.0.500
0.5in.
1.00
6.0in.
12in.0.500
4.0
1.00
2in.
12in.0.500
8.0in.
1.00
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
62/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
63/123
51
9.0in.
36in.
0.500in. 1.00 in.
2.0in.
9.0in.
36in.
0.500 in. 1.00 in.
6.0in.
9.0in.
36in.
0.500 in. 1.00in.
10.0 in.
*Transducerwasmounted
onleftendoftherod.
*Alltransitionswere90
asshownatright
90
Figure39. 3.0ft.long1.0in.diameterrodswith2.0in.,6.0in.,and8.0in.lengthsofsimulatedcorrosion
startingat9in.alongtherod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
64/123
52
Figure40. Peakfrequencyofthebackechofor3.0ft.longrodswith2.0in.,6.0in.,and10.0in.lengthsof
simulatedcorrosion.
percentageoftotalrodlength(Figure40). Theresultsshowanincreaseinpeakfrequencywith
anincreaseinpercentsimulatedcorrosion. The0.5in.and1.0in.diameterrodswithout
simulatedcorrosioncreatetheupperandlowerboundofthefrequencyshift. The1.0in.
diameterrodrepresentsarodwithoutanysimulatedcorrosionandformsthelowerboundof
thepeakfrequency. The0.5in.diameterrodrepresentsarodwithfull0.5in.diameter
simulatedcorrosionandformstheupperboundofthepeakfrequency. Theshiftinpeak
frequencyshowsthattheincreaseinsimulatedcorrosionlengthactsasafilterforcertain
frequenciesintheultrasonicsignal.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
65/123
53
Overall,theresultsindicatethatanincreaseinpeakfrequencyofthebackechooccurswithan
increaseinthelengthofsimulatedcorrosionfor1.0ft.and3.0ft.longrodswitha1.0in.
diameter. The3.0ft.longrodsexhibitedastrongercorrelationthanthe1.0ft.longrods,but
thenumberofdatapointsforeachrodlengthwaslimited.
4.3.2 ChangeinBackEchoAmplitudewithLengthofSimulatedCorrosionThemaximumamplitudesofthebackechoandthefirsttrailingechowereinvestigatedto
identifyarelationshipwiththelengthofsimulatedcorrosion.Thebackechorepresentsan
ultrasonicpulseundergoingdirectreflectionfromtheendoftherod,whilethefirsttrailing
echoincludesonemodeconversionwithshearwavepropagationacrosstheminimum
diameteroftherod.
Thesetof1.0ft.(Figure37)longrodswereusedfortesting. Thebackechoandfirsttrailing
echowererecordedforeachrod(Figure41).Themaximumamplitudesofthebackechoand
thefirsttrailingechowererecordedinTable9. Theratiooftheamplitudeofthefirsttrailing
echotothebackechoincreaseswiththelengthofsimulatedcorrosion. Theamplituderatiofor
eachlengthofsimulatedcorrosionwasplottedinFigure42. Theresultsshownastrong
correlationbetweenthepercentlengthofsimulatedcorrosionandtheratioofpeaktrailing
echotothebackecho. Theincreaseinamplitudeofthetrailingechorelativetotheamplitude
ofthebackechowasduetotheincreasedlengthofsimulatedcorrosion. Assumingapoint
sourceforatransducer,Figure43showsacrosssectionoftheultrasonicwavethatreflects
fromthesimulatedcorrosionregionfora0.5in.and8in.lengthofsimulatedcorrosion.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
66/123
54
Figure41. Backechoandfirsttrailingechofor1.0 ft.longrodswithmultiplelengthsofsimulatedcorrosion
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
67/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
68/123
56
0.5in.lengthofsimulatedcorrosion
8.0in.lengthofsimulatedcorrosion
Portionofwavethat
reflectsfromthesimulated
corrosionsurface
Figure43. Comparisonofreflectionfromthesimulatedcorrosionsurface
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
69/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
70/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
71/123
59
Figure46. Ultrasonicsignalfor90,45,30,15,10and5 transitionangles
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
72/123
60
Figure47. Delayindetectableflawechoversustransitionangle
theflawechodoesnotdecreaseconsistentlywiththetransitionangle. Thisphenomenonwas
investigatedmorethoroughlybymachiningrodswithamorecompleterangeoftransition
angles. Tocompareamplitudesbetweenvariousrods,thedatawasnormalizedusingnotches
tocomparetwoamplitudeswithinasingleultrasonicsignal. Multiplevariablesaffect
consistenttransducercoupling.Theseinclude:forceappliedtothetransducer(couplingforce),
surfaceconditionoftherodend,amountofcouplinggel,andthepresenceofparticles
betweenthetransducerandthesurfaceofthespecimen. Thesevariablesaredifficultto
controlconsistently. Tomaintainaconsistentcomparison,anotchwasaddedtoeachrodto
createarepeatablebaselineechoineveryultrasonicsignal. Thesignalechoassociatedwith
thereflectionfromthisnotchwascomparedtotheamplitudesofanyechoesofinterestin
ordertonormalizethedata. Threenotchlocationswereevaluatedtoselectanappropriate
baselinenotchlocation. Eachnotchwascutintoa1in.diameter,6in.longrod. Thenotchwas
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
73/123
61
made0.125in.deeparoundthecircumferenceoftherodandwas0.25in.wide(Figure48).
Thenotcheswerecutatthreedifferentdistancesfromtheleadingedgeoftherod:0.5in.,1.0
in.,and1.5in. Therodsweretestedwiththe5MHzmagnetictransducer,andtheultrasonic
signalwasrecorded(Figure49). Thenotchlocated1in.awayfromtheultrasonictransducer
wasselectedbecauseitprovidedanechothatcouldbemeasuredinthesameorderof
magnitudeastheflawechoesfoundinFigure46,anddidnotaddextranoisetotheultrasonic
signal. Incontrast,thenotchlocated2in.fromthetransducerprovidedincreasednoise
followingthebackecho,whilethenotchlocated0.5in.fromthetransducerprovidedapulse
withanegligibleamplitude.
0.5in.
6in.
0.75in.
0.25in.
1.00in.
1.0in.
6in.
0.75in.
0.25in.
1.00in.
0.5in.
6in.
0.75in.
0.25in.
1.00in.
Figure48. 6.0in.long1.0in.diameterrodswith0.125in.deep0.25in.widenotches
located0.5in.,1.0in.,and2.0in.fromtheendoftherod
Ultrasonic
Transducer
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
74/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
75/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
76/123
64
Figure51. Normalizedmaximumamplitudeofflawechoversustransitionangle
echo. Thenormalizedamplitudedecreasedsharplyfromatransitionangleof90to75.
However,insteadofcontinuingtodecline,thenormalizedamplitudeleveledoffandthen
showedseveralsmallpeaksalongwithasignificantpeakatatransitionangleof30anda
smallerpeakatatransitionangleofapproximately43. Thepeakswereinvestigatedusingthe
raymethod,assumingapointsourceattheendoftherod. Twopossiblescenarioswere
considered.
Thefirstscenarioconsideredwasthedirectlongitudinalwavereflectionfromthetransition
surface. AccordingtoSnell'slaw(Figure3),alongitudinalwavereflectsattheangleof
incidenceofthelongitudinalwavearrivalatthesurface,becausethewavespeedsarethesame
(Figure52). Table10documentstheangleoftravelofthereflectedlongitudinalwavewith
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
77/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
78/123
66
Table10. Angleoflongitudinalwavereflectionfromtransitionsurface
TransitionAngle InitialWaveAngle IncidentAngle ReflectedWaveRelativetoRodAxis
transition initial 1 axis
5
4.76
80.24 165.2410 4.76 75.24 155.24
15 4.75 70.25 145.25
20 4.73 65.27 135.27
25 4.71 60.29 125.29
30 4.69 55.31 115.31
35 4.67 50.33 105.33
40 4.64 45.36 95.36
42.5 4.62 42.87 90.00
45 4.61 40.39 85.39
50 4.58 35.42 75.42
55 4.55 30.45 65.45
60 4.51 25.49 55.49
65 4.48 20.52 45.52
70 4.44 15.56 35.56
75 4.40 10.60 25.60
80 4.36 5.64 15.64
85 4.33 0.67 5.67
90 4.29 4.29 4.29
Thesecondscenarioconsideredwasthedirectshearwavemodeconversionfromthetransition
surface. Theinitiallongitudinalwavemodeconvertsatthetransitionsurfaceproducingashear
wavereflection. AccordingtoSnell'slaw,theshearwavereflectsatanincidentanglethatis
dependentuponthearrivalincidentangleandthespeedsofthelongitudinalwave(C1)and
shearwave(C2)(Figure53). Table11documentstheangleoftravelofthereflectedshearwave
withrespecttotheaxisoftherod. Whentheshearwavereflectsfromthetransitionsurface
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
79/123
67
ata90angletothelongitudinalaxisoftherod,thewavereflectsfromtheoppositetransition
surfaceonemoretimeandreturntothepointsource,duetosymmetry. This90reflection
occursata27.8transitionangle. Thisrepresentsthelargepeakatapproximately28in
Figure51. Thevaluewasapproximatebecausethetransducerwasapproximatedasapoint
source.
Figure53. Shearwavereflectionfromtransitionsurface
initial
tansition
1
2
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
80/123
68
Table11. Angleofshearwavereflectionfromtransitionsurface
Transition
Angle
Initial Wave
Angle
Incident
Long.Angle
Incident
ShearAngle
ReflectedWave
RelativetoRodAxis
transition initial 1 2 axis
5 4.76 80.24 32.95 117.95
10 4.76 75.24 32.26 112.26
15 4.75 70.25 31.30 106.30
20 4.73 65.27 30.09 100.09
25 4.71 60.29 28.64 93.64
27.8 4.70 57.50 27.71 90.00
30 4.69 55.31 26.99 86.99
35 4.67 50.33 25.14 80.14
40 4.64 45.36 23.12 73.12
45 4.61 40.39 20.95 65.95
50 4.58 35.42 18.66 58.6655 4.55 30.45 16.24 51.24
60 4.51 25.49 13.74 43.74
65 4.48 20.52 11.16 36.16
70 4.44 15.56 8.51 28.51
75 4.40 10.60 5.83 20.83
80 4.36 5.64 3.11 13.11
85 4.33 0.67 0.37 5.37
90 4.29 4.29 2.37 2.37
Overall,theresultsprovideevidencetosupporttwoconclusions. First,exceptforthe27.5
transitionangle,theflawechoexperiencedasignificantdecreaseinamplitudebelow80but
wasstilldetectable. Theflawechowasdetectableforgradualtransitionsaslowas5.
Second, transitionscauseadelayintheultrasonicsignalbetweenthemainbangandtheflaw
echo. Themoregradualthetransition,thelongerthedelay. Thelargestdelaywas23.8sfor
the5transitionwhichcorrespondstoa5.5in.insteelrods. Thus,thelocationofsimulated
corrosionmustbeadjustedbaseduponthetransitionangleofthesimulatedcorrosion.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
81/123
69
5 WilliamsCommercialTiebackRodTestingTherodstestedtoevaluatethephysicalgeometryofsimulatedcorrosionweremachinedfrom
12L14smoothrodstock. Commerciallyavailabletiebackrodsaretypicallyfabricatedwithan
allthreadsurface.Williamscommercialtiebackrodswereselectedfortestingtoevaluate
differencesintheultrasonicsignalduetothethreadedsurface.
5.1 TypesofTiebackRodsUsedinGeotechnicalApplicationsVariousstylesoftiebackrodshavebeenusedinconstructionofsheetpilesystems. Thetwo
mostcommonstylesareshownbelow(Figure54). Theupsetthreadstylewascommonin
previousconstruction. Upsetthreadsarerolledintothesteelrod,ratherthancut,toensure
theminordiameterofthethreadsisgreaterthantheouterdiameteroftherod. These
tiebackrodsweretypicallyfabricatedfromsmoothA36steelrod. Themajorityofcurrent
geotechnicalpracticesuseallthreadtiebackrods. Thesetiebackrodsarefabricatedfroma
highgradesteelwiththreadsformedalongtheentirelengthoftherod.
Rods used in old construction
(Upset Threads)
Rods used in new construction
(All-Thread)
Figure54. Upsetthreadandallthreadrods
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
82/123
70
Theultrasonicsignalsfor12L14smoothrodstockandWilliamsallthreadrodswerecompared.
Therodstestedwere10feetlongwitha1.0in.majordiameter. Thefullultrasonicsignalfor
eachtypeofrod,includingmultiplebackechoes,isprovidedinFigure55. Adistinctdifference
Figure55. Comparisonof10ft.longWilliamsthreadedrodand12L14smoothsteelrod
isevidentin theportionofthesignalfollowingeachbackechoforthetworods. Figure56
providesacloserlookatthebackechoandsubsequenttrailingechoesofeachrod.The
ultrasonicsignalforthe12L14steelrodshowsseveraldistincttrailingechoesaftertheback
echo.TheWilliamstiebackrodshowsadistinctbackechowithonlyonedistinguishabletrailing
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
83/123
71
echo. Thetimebetweenthebackechoandthetrailingechowasdifficulttomeasureinthe
Williamsthreadedrodduetoincreasednoiseintheultrasonicsignal. ThreadsintheWilliams
rodcausedispersionoftheultrasonicwaveduetospuriousreflectionsfromthethreaded
surfaces. Sincetrailingechoesinvolveatleastonereflectionfromthesurfaceoftherod,
detectingtrailingechoesfromathreadedsurfaceprovestobedifficult. Thisimpliesthat
calculatingtheexactouterdiameterofathreadedrodmaynotbepossibleusingthetime
betweentrailingechoes(t). Anapproximationofthediametermaybecalculatedusingthe t
betweenthepeaks,insteadoftheleadingedge,ofbackechoandthefirsttrailingecho.
Figure56. Trailingechocomparisonfor12L14smoothrodandWilliamsthreadedrod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
84/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
85/123
73
evaluatingthepeakvaluesofsuccessivebackechoesineachrod. ArectifiedAscan,which
acquirestheabsolutevalueoftheultrasonicsignalamplitude,includingalldetectableback
echoes,wasrecorded(Figure57). Theattenuationofthewaveamplitudealongtherodwas
definedbyEquation29(Kolsky,1963)
Equation29
whereaoistheinitialamplitude, isthecoefficientofattenuation,andxisthedistancealong
therod. TheunitsofthecoefficientofattenuationareNepers(Np)perlength,whereaNeper
isadimensionlessquantity. Thepeakamplitudeofeachbackechowasplottedwithrespectto
thedistancetraveled(Figure58.) Thebestfittrendlinewascalculatedanddisplayedwiththe
Figure58. Signalattenuationfor1.0ft.,3.0ft.,and6.0ft.longWilliamsrods.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
86/123
74
equationandR2value. Theattenuationcoefficients()forthe1ft.,3ft.,and6ft.rodswere
0.177Np/ft.,0.120Np/ft.,and0.096Np/ft.respectively. Thedifferencesinmagnitudeof
wereduetoscatteringwhichoccurredeachtimetheultrasonicwavereflectedfromanendof
therod. Whentheultrasonicwavetraveledanequivalent12feetalongthe1ft.longrod,the
wavereflectedfromanendsurface11times. Forthe3ft.and6ft.longrods,thesame12ft.
equivalentlengthincluded3and1endreflectionsrespectively. Theresultsshowadecreasein
attenuationcoefficientwithadecreaseinthenumberofendsurfacereflections. Longerrods
havefewerreflectionsresultinginasmallerattenuationcoefficient.
Figure55showsthata10ft.long1.0in.diameterWilliamstiebackrodexhibits4distinctback
echoesintheultrasonicsignal. Thisshowsthatthepulseechomethodusinga5MHzprobe
couldbeusedtodetectabackechoina1.0in.diameter40ft.longWilliamstiebackrod. This
wasaconservativeestimatesinceanactual40ft.rodwouldnotincludetheattenuationfrom
themultipleendreflectionsinthe10ft.rod.
5.3 SignalAttenuationforWilliamsRodsinSoilTheeffectofultrasonicsignalattenuationinsoilwasimportantfortestingWilliamscommercial
tiebackrods. Theamountofenergytransmittedintothesurroundingmediumduringultrasonic
inspectionofatiebackrodisdependentuponthepropertiesofthatmedium. Williamstieback
rodswithvarioussurroundingmediaweretestedtoinvestigatetheeffectonsignal
attenuation. Threesectionsof3ft.longWilliamstiebackrodswereplacedinplywoodboxes
withapproximately5.5in.ofcoverineachdirection. Anultrasonictransducerwascoupledto
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
87/123
75
oneendofthetiebackrodwhichprotrudedthroughtheendofthebox(Figure59). Eachbox
wasfilledwithoneofthreesoils: sand,loosesoil,andcompactedsoil.
Figure59. Boxesconstructedforsignalattenuationtestsinsoils
5.3.1 SoilCharacterizationTwosoils,sandandPalousesoil,wereusedinthetests. Thesandwascollectedfromaquarry
runbyAtlasConcretecompanyinLewiston,Idaho. ThePalousesoilwascollectedfromtopsoil
inthePalouseregionofWashingtonState. Thesoilswerecharacterizedaccordingtothe
protocoldevelopedbytheArmyCorpsofEngineersforearthretentionssystems,including
grainsizedistributionandAtterberglimittests(USArmyCorpsofEngineers,1994).
AgrainsizedistributiontestwasperformedaccordingtoASTMD422(ASTMStandardD422,
2007). TheresultswereplottedforeachsoilinFigure60andthecoefficientofuniformity(Cu)
andcoefficientofcurvature(Cc)werecalculatedforeachsoil. Theresultswererecordedin
Table12.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
88/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
89/123
77
Figure61. AtterberglimittestofPalousesoil
experimentaldatausedtodeterminetheliquidlimit(LL). Theplasticlimit(PL)wasmeasured
experimentallyandtheplasticityindex(PI)andtheflowindexwerecalculatedusingLLandPL.
TheresultswereprovidedinTable13.
Table13. ResultsofAtterberglimittestforPalousesoil
PL 23.4
LL 35.3
PI 11.9
Flow Index -1.33
Usingthesoilpropertiesmeasured,theUSCSsoilclassificationwasdeterminedforsandand
Palousesoil. Thesandusedwasapoorlygradedsand(SP)and thePalousesoilwasasiltysand
(SM).
5.3.2 SoilPreparationThesandandloosesoilwereplacedintheboxescompletelysurroundingtheWilliamstieback
rods. Forthesandandloosesoilnocompactionwasused. Forthecompactedsoila25lb.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
90/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
91/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
92/123
80
Table15. AttenuationcoefficientsoftheultrasonicsignalforWilliamstiebackrodsinsoils
Sand LooseSoil CompactedSoil
Control Baseline Wet Control Baseline Wet Control Baseline Wet
0.081 0.075 0.078 0.072 0.069 0.065 0.095 0.076 0.0830.074 0.084 0.08 0.068 0.069 0.074 0.094 0.076 0.082
0.084 0.083 0.087 0.066 0.073 0.073 0.083 0.079 0.071
0.079 0.082 0.085 0.065 0.072 0.07 0.083 0.076 0.07
0.079 0.08 0.079 0.064 0.076 0.075 0.093 0.095 0.089
0.083 0.08 0.078 0.077 0.075 0.067 0.081 0.09 0.089
0.08 0.083 0.081 0.073 0.075 0.061 0.088 0.08 0.083
0.079 0.073 0.081 0.073 0.073 0.073 0.089 0.081 0.083
0.083 0.079 0.086 0.075 0.086 0.076 0.093 0.075 0.09
0.081 0.067 0.082 0.072 0.086 0.067 0.084 0.075 0.091
Average Average Average Average Average Average Average Average Average
0.0803 0.0793 0.0817 0.0705 0.0754 0.0701 0.0883 0.0803 0.0831
Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev.
0.0029 0.004 0.0033 0.0045 0.0061 0.0049 0.0053 0.0069 0.0074
CoV CoV CoV CoV CoV CoV CoV CoV CoV
0.0361 0.0504 0.0404 0.0638 0.0809 0.0699 0.0600 0.0859 0.0890
zTest zTest zTest zTest zTest zTest
0.640 1.008 2.044 0.190 2.908 1.807
theloosesoilthecoefficientsofattenuationswere0.0705Np/ft.,0.0754Np/ft.,and0.0701
Np/ft.forthecontrol,"baseline",and"wet"samples. Again,therewasnosignificantincrease
inattenuationfromthecontroltothe"baseline"or"wet"condition. Forthecompactsoilthe
coefficientsofattenuationwere0.0883Np/ft.,0.0803Np/ft.,and0.0831Np/ft.forthecontrol,
"baseline",and"wet"samples.Inthiscasetheattenuationcoefficientsforthe"baseline"and
the"wet"conditionwereslightlylessthanthecoefficientofattenuationforthecontrol. Thez
Testforeach"baseline"and"wet"testcomparedwiththecontrolshowedthatalltests,except
the"baseline"forthecompactedsoil,werewithina99%confidenceinterval (2.58z2.58).
NormalizeddataisalsoshowninTable16whichiscalculatedbydividingeachofthe"baseline"
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
93/123
81
and"wet"conditiontestsbytheaveragecontrolvalueforeachrod. Forexample,theaverage
"baseline"valueforsandof0.979showsthattheattenuationcoefficientwas97.9%ofthe
averagecontrolvalue. Theseresultsshowthattheattenuationcoefficientforthe"baseline"
and"wet"conditionoftheultrasonicsignalforsand,loosePalousesoil,andcompactPalouse
soilwaswithinplusorminus9.1%forpercentwatercontentsupto7.74%,28.21%,and29.50%
respectivelyforWilliamstiebackrods.
Table16. NormalizedattenuationcoefficientsoftheultrasonicsignalforWilliamstiebackrodsinsoils
Sand
LooseSoil Compacted
Soil
Baseline Wet Baseline Wet Baseline Wet
0.934 0.971 0.979 0.922 0.861 0.940
1.046 0.996 0.979 1.050 0.861 0.929
1.034 1.083 1.035 1.035 0.895 0.804
1.021 1.059 1.021 0.993 0.861 0.793
0.996 0.984 1.078 1.064 1.076 1.008
0.996 0.971 1.064 0.950 1.019 1.008
1.034 1.009 1.064 0.865 0.906 0.940
0.909 1.009 1.035 1.035 0.917 0.940
0.984 1.071 1.220 1.078 0.849 1.0190.834 1.021 1.220 0.950 0.849 1.031
Average Average Average Average Average Average
0.979 1.017 1.070 0.994 0.909 0.941
Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev. Std.Dev.
0.067 0.041 0.086 0.070 0.078 0.084
CoV CoV CoV CoV CoV CoV
0.069 0.040 0.080 0.070 0.085 0.090
Thepercentoftheincidentwavethatistransmittedtothesurroundingmediaduringa
reflectionisdependentupontheimpedanceofthetwomaterialsincontact(Krautkramer&
Krautkramer,1990). Ifthetwomaterialshavethesameimpedanceandareinperfectcontact,
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
94/123
82
thenalltheenergywilltransferthroughtheboundary. Thetransmittancepercentfortwo
dissimilarimpedancesisgivenby
Equation30
whereZ1istheimpedanceofthesteel(Z=46.0MRayls)andZ2istheimpedanceofthe
surroundingmedia,forthematerialsinthisstudy. Figure63showsthetransmittanceofasteel
rodembeddedinseveral surroundingmediaincludingwater(Z=1.48MRayls)andconcrete(Z
=8.0MRayls). Foratiebackrodinsoil,partofthesurroundingmediais air(Z=0.000429
MRayls),whichdrasticallydecreasesthetransmittanceoftheincidentwavetothesurrounding
media. Consideringthataportionofthesurroundingmediaisairandthefirstbackechoonly
hasonereflection,thetransmittanceisnegligible. Thus,theinspectablelengthsoftiebackrods
willnotvarywhentherodsareembeddedinsoils.
Figure63. Transmittanceforsteelwithwaterandconcretesurroundingmedia
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
95/123
83
5.4 ActualTiebackRodswithFlawsSimulatedcorrosionwasmachinedin3ft.Williamstiebackrodsectionstodetermineifspecific
geometriescouldbedetectedincommercialtiebackrods. Theseincludedlocationof
simulatedcorrosion,diameterofsimulatedcorrosion,lengthofsimulatedcorrosion,andthe
transitionofsimulatedcorrosion.
5.4.1 LocationofSimulatedCorrosionThreeWilliamssteelrods,3ft.longand1in.indiameter,weremachinedwithsimulated
corrosionatvariouslocationstovalidatethepulseechomethodforlocationtheleadingedge
ofsimulatedcorrosioninaWilliamstiebackrod. Simulatedcorrosionwitha0.5in.diameter
9.28in.
36in.
0.500in. 1.00 in.
2.0in.
15.97in.
36in.
0.500 in. 1.00 in.
2.0 in.
22.84in.
36in.
0.500 in. 1.00in.
2.0 in.
*Transducerwasmounted
onleftendoftherod.
*Alltransitionswere90
asshownatright
90
Figure64. 3.0ft.long1.0in.diameterWilliamstiebackrodswith2.0in.lengthof0.5in.simulatedcorrosion
diameterat9.28in.,15.97in.,and22.84in.alongtherod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
96/123
84
and 2.0in.lengthwasmachinedat9.28in.,15.97in.,and22.84in.alongthelengthofthe
steelrods(Figure64).Thelocationofsimulatedcorrosionwaseasilydetectablebasedonthe
timebetweenthemainbangandtheleadingedgeoftheflawecho. Thefollowingsignals
(Figure65)showaflawechoappearingintheultrasonicsignalthatcorrelatesdirectlywiththe
locationoftheflaw. Theformulaforlength(Equation27)wasusedtodeterminethelocation
oftheflaw(Table17)foreachofthethreerodsinFigure65. Thethreerodsshoweda
maximumpercentdifferenceof1.59%betweenmeasuredandcalculatedflawlocation. The
Figure65.Ultrasonicsignalsfrom3.0ft.long1.0in.diameterWilliamstiebackrodswith2.0in.lengthof0.5in.
diametersimulatedcorrosionat9.28in.,15.97in.,and22.84in.alongtherod.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
97/123
85
resultsshowthattheabilitytolocatetheflawpositionwasnotaffectedbythethreadsofthe
Williamsrods.
Table17. Comparisonofmeasuredandcalculatedlocationofsimulatedcorrosion
MeasuredFlawLocation
(in.) FlawTime(s) CalculatedFlawLocation(in) %Difference
9.28 79.3 9.13 1.59%
15.97 138.3 15.93 0.27%
22.84 197.4 22.73 0.47%
5.4.2 DiameterofSimulatedCorrosionToverifythedetectionofsimulatedcorrosiondiameteronWilliamstiebackrods,two3ft.long
rodsweremachinedwith0.5in.diameterand0.75in.diametersimulatedcorrosionregions
16.0in.
36in.
0.500 in. 1.00 in.
2.0 in.
*Transducerismounted
onleftsideofrod.
*Alltransitionsare90asshownatright
90
Figure66. 3.0ft.long1.0in.diameterWilliamsrodswith2.0in.lengthsof0.5in.and0.75in.diameter
simulatedcorrosion
16.0in.
36in.
0.750 in. 1.00 in.
2.0 in.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
98/123
86
Figure67. ComparisonofWilliamsrodswith0.5in.and0.75in.diameterofsimulatedcorrosion
(Figure66). Thefirstbackechowitheachdistinguishabletrailingechoeswasprovidedin
Figure67. Thetimebetweenthetrailingechoeswasmeasured(Table18.) UsingEquation25
thediameterwascalculatedfromthespacingofthetrailingechoes. The0.5in.simulated
corrosiondiameterrodhadacalculateddiameterof0.51in.resultingina1.9%difference. The
0.75in.simulatedcorrosiondiameterrodhadacalculateddiameterof0.73resultingina2.6%
difference. Thisprovidesaverystrongcorrelationbetweentheminimumdiameter(or
simulatedcorrosiondiameter)andthetimebetweentrailingechoesfortheWilliamsrod.
Table18. Timebetweentrailingechoesfor0.5in.and0.75in.simulatedcorrosiondiameter
RodSmallest
Diameter(in.)
Measured
Time(s)
Calculated
Diameter(in.)
%Difference
0.5in.SimulatedCorrosion 0.50 3.34 0.51 1.9%
0.75in.SimulatedCorrosion 0.75 4.79 0.73 2.6%
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
99/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
100/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
101/123
89
5.4.4 TransitionofSimulatedCorrosionFinally,a3ft.longWilliamsrodwasmachinedwitha0.5in.simulatedcorrosiondiameteranda
45transitionangle(Figure71). Thisrodwasusedtoinvestigatetheabilitytodetectthe
location,diameter,andlengthofsimulatedcorrosionforarodwitha45transitionangleina
Williamsrod. ThefullultrasonicsignalfromthepulseechotestwasrecordedfortheWilliams
rodwitha45transition(Figure72). Thesignalshowsadistinctflawandbackecho. Theflaw
andbackechowereeachfollowedbyfourdistincttrailingechoes.
Figure72. Fullultrasonicsignalfor2in.lengthof0.5in.diametersimulatedcorrosionwith45transitionangle
forWilliamstiebackrod
*Transducerismounted
onleftsideofrod.
45o
36in.
15.75in. 0.500 in. 1.00 in.
2.0 in.
Figure71. Rodusedforsimulatedcorrosiondetectionwitha45transitionangle
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
102/123
90
Thearrivaltimeoftheflawechowas138.7s. Usingthelongitudinalwavespeedofthe75ksi
steel,theflawlocationwascalculatedtobe15.97in,whichhasa1.41%differencefromthe
measured15.75in.tothebeginningofthetransitionoftheflaw(Table19). Thisshowsthatthe
methodusedinthepreviouschapterforlocatingthepositionofsimulatedcorrosioncanbe
usedinWilliamsrodswitha45transitionangle.
Table19. CalculatedsimulatedcorrosionlocationforWilliamsrodwith45transitionangle
MeasuredFlawLocation
(in.) FlawTime(s) CalculatedFlawLocation(in) %Difference
15.75 138.7 15.97 1.41%
ThebackechoandsubsequenttrailingechoeswererecordedfortheWilliamsrodwitha45
transitionangle. Thebackechoandfourtrailingechoeswerevisible(Figure73.) Thearrival
timeofthefirstbackechoandtwotrailingechoeswereusedtocalculatethetimebetween
echoes. Thistimebetweentrailingechoeswasusedtocalculatethediameterofthesimulated
Figure73. Firstbackechoandsuccessivetrailingechoesfor2in.simulatedcorrosionwith45transition
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
103/123
91
corrosionaccordingtoEquation25(Table20). Thecalculateddiameterwas0.502in.whichhad
a0.4%differencefromthemeasuredvalueof0.500in. Thisshowsthatthemethodfor
detectingthediameterofsimulatedcorrosioncanbeusedforWilliamsrodswitha45
transitionangle.
Table20. ComparisonofmeasuredandcalculateddiameterofsimulatedcorrosionforWilliamsrodwith45
transitionangle
RodSmallest
Diameter(in.)
MeasuredTime
(s)
Calculated
Diameter(in.)%Difference
0.5in.simulatedcorrosion 0.500 3.27 0.502 0.4%
TheFFTofthefirstbackechowasrecordedfortheWilliamsrodwitha2in.lengthofsimulated
corrosionanda45transitionangle. TheresultwasplottedwiththeFFTsignalsfroma0.5in.
diameterand1.0in.diameter3.0ft.longrodsof12L14steel. Theresultsshowthatthe
Figure74.Frequencyofbackechoof2in.long0.5in.diametersimulatedcorrosionwith45
transitioninWilliamsrod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
104/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
105/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
106/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
107/123
95
measuredfromtheleadingedgeofthemainbangtotheleadingedgeoftheflawecho. The
leadingedgeforeachechoisdefinedasthefirstpointthatappearsoutsidetheboundsofthe
signalnoise. Figure77plotseachpointoftheultrasonicsignalintherangeofthemainbang
andtheflawechotoidentifytheleadingedge. Forrodswithatransitionfromtheoriginal
diametertotheflawdiameter,themeasuredtimemayincludeadelayfromtheactualflaw
location. Themaximumdelayfora5transitionangleina1.0in.diameterrodwith0.5in.
diametersimulatedcorrosionwas23.8s,whichcorrespondstoanerrorof0.44in.for
determiningthelocationoftheflaw.
Figure78depictsthebackechoandtrailingechoesfora3.0ft.long1.0inchdiameter12L14
smoothsurfacerodandaWilliamscommercialtiebackrod,bothwitha2.0in.longsectionof
0.5in.diametersimulatedcorrosionstarting17.0in.fromtheleftendoftherod. Thetime
betweenthetrailingechoesfollowingthefirstbackechocanbedirectlyrelatedtothediameter
Figure78. Firstbackechoandsubsequenttrailingechoesforinspectionofsimulatedcorrosiondiameter
inspectionin1.0in.diameter12L14steelrodand1.0in.diameterWilliamsrod
12L14SteelRod
WilliamsTiebackRod
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
108/123
96
ofsimulatedcorrosion. Equation31correlatesthediameteroftherod(d)tothetimebetween
echoes(t),baseduponthespeedoflongitudinalwavepropagation(C1)andthespeedof
transversewavepropagation(C2). Thetimebetweentrailingechoesismeasuredinthesame
Equation32
mannerasthetimebetweenthemainbangandtheflawecho. Theindividualpointsofeach
echoareplottedtoidentifytheleadingedgewhichisthefirstpointtoraiseaboveorbelowthe
noiseofthesignal. TypicalvaluesforthelongitudinalandshearwavespeedinsteelareC1=
19,190ft/sandC2=10,597ft/s. Thediameterofsimulatedcorrosioncanbeusedin
conjunctionwiththeoriginaldiametertodeterminethereductioninloadcapacity. Equation
32depictsthepercentloadcapacityfora rodwithsimulatedcorrosion.
%
Equation33
Theloadcapacityisdependentuponthediameterofthecorrodedregion,dc,andtheoriginal
roddiameter,do. Theabilitytoidentifythelocationanddiameterofcorrosionprovidesan
inspectorwiththeabilitytoapproximatethestructuralintegrityofatiebackrod.
Theselectionoftheultrasonictransduceriscriticalwheninspectingatiebackrod. Themain
variables toconsiderincommercialtransducersarethediameterofthetransducerandthe
frequencyoftheultrasonicsignalgenerated. Thetransducerdiametershouldbeaslargeas
possiblewithoutexceedingthediameteroftherod. Anincreaseinthediameterofthe
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
109/123
97
transducerresultsinanincreaseintheenergygeneratedintheultrasonicwavewhichinturn
increasestherangeofinspection.Thetransducerwavelengthisdependentuponthediameter
ofthetiebackrodandthesmallestexpectedflawdimension. Toensurebulkwavepropagation
thetransducerwavelengthshouldbeatleastoneorderofmagnitudelessthanthediameterof
therod. Thewavelengthoftheultrasonicsignalwilldeterminetheminimumflawdetectablein
thespecimen. Theminimumdetectableflawdimensionisapproximatelythewavelengthofthe
ultrasonicpulsefrequencyintroducedintothemedium(Figure17). Thesetwocriteriawill
determinethetransducerfrequencyselection.
Figure79. Minimumdetectableflawdimensioninsteel
6.2
Endpreparation
and
Transducer
Coupling
Asignificantvariationintheamplitudeofthesignalcanoccurduetotheconditionoftherod
end. Ifthesurfaceisnotplanar,thewavewillexperiencedispersionfromareflectionfromthe
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
110/123
98
endoftherod. Anothersourceofamplitudelosscanoccurinthecouplingofthetransducerto
therod. Itisimperativetohaveasmoothplanarsurfacetoattachthetransducer. Thus,itmay
benecessarytocutanewsurfaceattheendoftherod. Also,contaminantslocatedbetween
thetransducerandtheendoftherodmayresultinpoortransferofenergytotherod.
Therefore,theendofeachrodmustbecleaned,andacouplantgelappliedbeforethe
transduceriscoupledtotheendoftherod. Withoutthegel,thetransducerwillnoteffectively
coupletheultrasonicsignalintotherod,resultinginanextremelypoorultrasonicwave,ifany
atall. Amagnetictransducerisalsorecommendedtoprovideaconsistentadheringforce
betweenthetransducerandtheendoftherod.
6.3 CommercialTiebackRodTestingThefollowingguidelinesarepresentedtoassistindevelopinganinspectionprocedurefor
tiebackrodsinthefield. Transitioningfromtestingsmooth12L14samplestoinsitutestingof
commercialtiebackrods introducesseveralpotentiallimitations. First,turnbucklesareoften
usedwhenadesigncallsforrodslongerthan50ft. Anultrasonicsignalisnotabletopropagate
throughtheturnbuckle,thusonlythefirstsectionofrodisinspectable. Second,actual
corrosionwillnothaveasmoothsurface,orasinglediameter. Theirregularsurfaceofactual
corrosionwillincreasescatteringoftheultrasonicwaveduringreflection. Third,curvaturein
thetiebackrodmayeliminatethedetectionofthebackecho.Ifadirectlineofsightthrough
therodfromthefronttothebackoftherodiseliminatedthendetectionofadirectbackecho
isnotpossible. Thesefactorsmaylimittheeffectivenessofultrasonicinspectioninsome
scenarios. Thefollowingchartsprovideguidelinesfortheuseoftheultrasonicpulseecho
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
111/123
99
methodforinspectingtiebackrods. Theguidelinesaredividedintotwosections. Thefirst
sectioncoversinspectionsofnewconstruction. Theseguidelinesassumethatinitialultrasonic
pulseechomeasurementswillbeperformedaftertheplacementoftherodsandpriortothe
facadeconstruction,whichcoverstheendsofthetiebackrods. Thesecondsectioncovers
inspectionofexistingconstruction. Thissectionisdividedintotwosections. Thefirstsub
sectionincludestiebackrodlengthsthatarerecordedinthedesignplans. Thesecond section
isforinspectionoftiebackrodswithunknownlength.
6.3.1 NewConstruction
Thissectionintroducesinspectionguidelinesfortiebackrodsinnewconstruction. Performing
severalmeasurementsduringtheconstructioncansignificantlyincreasetheabilitytomonitor
corrosioninsteeltiebackrods. Anultrasonicpulseechomeasurementperformedafterthe
placementoftherods,andpriortothefaadeconstructiongeneratesa"controlsignal"to
comparewithsubsequentmeasurementsduringthelifeoftherod. Thecontrolsignalshould
includetwoseparateinspections. First,afullsignalshowingalldetectablebackechoes,and
secondthefirstbackechowithalldetectabletrailingechoes. Thefullsignalcanbeusedto
calculatetheactuallongitudinalwavespeedofeachrod,usingthetimebetweenthemain
bangandthefirstbackecho. Apublishedvaluefortheshearwavespeed,C2=10,597ft/swill
beused. Thefollowingisaseriesofstepstoaidinfutureinspections:
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
112/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
113/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
114/123
102
6.3.2 ExistingConstructionInterpretationofinspectionofexistingconstructionismoredifficultthannewconstruction.
Sincethereisnotacontrolsignalgeneratedduringtheconstructionprocess,theseguidelines
mustbedividedintotwosubcategories. Thefirstapproachassumesthattheoriginalplansare
availablewhichidentifytheoriginalrodlength. Thesecondapproachisforinspectionofrods
ofunknownlength.
6.3.2.1 OriginalrodlengthisknownRodswithaknownlengthprovidedimensionstoidentifythebackechointheultrasonicsignal.
Thefollowingisseriesofstepstoaidininspectionoftiebackrodsofknownlength:
Step#1: Calculatethetimebetweenthemainbangandthebackecho
UsingthelengthoftherodandalongitudinalwavespeedofC1=19,190ft/scalculatethe
expectedtimebetweenthemainbangandthebackechousingEquation30.
Step#2:Performapulseechoinspectiononthetiebackrod
Recordthreedifferentsectionsoftheultrasonicsignal. First,recordthefullsignal,extendingto
thefirstbackwithalldetectabletrailingechoes. Usetheexpectedtimefromthemainbangto
thetrailingechofromStep#1toapproximatethetimewindownecessarytocapturetheentire
signal. Second,recordthebackechowithalldetectabletrailingechoes. Third,recordanyflaw
echothatappearsbeforethebackechoandalldetectabletrailingechoes.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
115/123
103
Step#3: Verifythelengthofthetiebackrod
Measurethetimebetweenthemainbangandthebackechointheultrasonicsignal. Usethis
measurementtocalculatethelengthoftherod,usingalongitudinalwavespeedofC1=19,190
ft/swithEquation30. Comparethecalculatedrodlengthwiththeoriginalrodlengthtoensure
thattherearenocompletebreaksintherod.
Step#4: Verifytheouterdiameterofthetiebackrod
Ifaflawechodoesnotexist,calculatethetimebetweentrailingechoesafterthebackecho. If
aflawechoexists,calculatethetimebetweentrailingechoesaftertheflawecho. Usingthe
appropriatetimebetweentrailingechoesandEquation31,calculatethediameteroftherod.
Measuringthetimebetweentrailingechoesmaybedifficultforthreadedrods,becausethe
threadscausedispersionoftheultrasonicwavewhenitreflectsandmodeconvertsfromthe
outerdiametertocreatethetrailingechoes.
Step#5: Calculatethelocationoftheflaw(ifaflawechoexists)
Measurethetimebetweenthemainbangandthefirstflawecho. Usethismeasurementto
calculatethedistancetotheflaw,usingalongitudinalwavespeedofC1=19,190ft/swith
Equation30. Repeatthisstepforeachdistinctflawecho. Becarefulnottomistakeasecond
flawechoassecondflaw. Anechothatappearsattwicethedistanceofthefirstflawismost
likelyasecondflawechoandnotasecondflaw.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
116/123
104
Step#6Determinetheminimumdiameterofthetiebackrod(ifaflawexists)
Measurethetimebetweenthebackechoandthefirsttrailingecho. Usethismeasurementto
calculatetheminimumdiameteroftherod,usingthelongitudinalwavespeedofC1=19,190
ft/s,andashearwavespeedofC2=10,597ft/s withEquation30.
6.3.2.2 UnknownlengthofrodArodwithunknownlengthrequiresacloseinspectionofthetrailingechoestoidentifypossible
flawsintherod. Thefollowingisseriesofstepstoaidininspectionoftiebackrodsofunknown
length:
Step#1:Performapulseechoinspectiononthetiebackrod
Recordthreedifferentsectionsoftheultrasonicsignal. First,recordthefullsignal,includingall
detectableechoes. Second,recordthefurthestechowithalldetectabletrailingechoes. Third,
recordanyotherechothatappearsinthesignalwith alldetectabletrailingechoes.
Step#2:Determineifnodetectableflawsarepresent
Measurethetimebetweentrailingechoesforeachechorecorded. Usingthetimebetween
trailingechoes,alongitudinalwavespeedofC1=19,190ft/s,ashearwavespeedof10,597ft/s
andEquation31calculateadiameterforeachsetoftrailingechoes. Ifthecorresponding
diameterforthefirsttwosetsoftrailingechoesisapproximatelyequaltotheoriginaldiameter
oftherod,thentheechoesrepresentthefirstandsecondbackechoes. Sincenoflawechoes
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
117/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
118/123
106
7 SummaryandConclusionsThisdissertationconcentratedonthedetectionofsimulatedcorrosioninsteeltiebackrods.
Ultrasonicsignalswereusedtodeterminethephysicalgeometryof0.25in.,0.50in.,and0.75
in.diametersimulatedcorrosionin1.0in.diametersteelrods. Researchwasalsoperformedto
investigatetheuseofultrasonicwavesinWilliamscommercialtiebackrods. Guidelineswere
developedforinspectingtiebackrodswithactualcorrosioninfieldapplications.
Thelocation,diameter,length,andtransitionofconcentricsimulatedcorrosionwere
investigatedforstraightsteelrods. Fora90transitionangle,thelocationofsimulated
corrosionwasdetectablebaseduponthetimebetweenthemainbangandtheflawechointhe
ultrasonicsignalandthelongitudinalwavespeedofthesteel. Adecreaseinthetransition
angleresultsinadelayinthearrivaltimeoftheflawecho. Thelargestdelaywas23.8sfor
the5transitionwhichrepresentsapotentialerrorof5.5in.whenestimatingthelocation.
Theminimumdiameterofconcentricsimulatedcorrosioninastraightrodwasdetectable
baseduponthedistancebetweenthebackechoandthefirsttrailingecho,andthelongitudinal
andshearwavespeedsofthesteelinaccordancewithpreviousresearchbyLight&Joshi(Light
&Joshi,1987). Thetimebetweenthebackechoandfirsttrailingechoisexclusivelydependent
upontheminimumdiameteroftherod,andisnotdependentuponthetransitionangleofthe
simulatedcorrosion.
Thelengthofconcentricsimulatedcorrosioninastraightrodwasdetectablebasedontwo
differenttechniques. First,anincreaseinthepeakfrequencyofthebackechocorrelatedwith
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
119/123
107
anincreaseinthelengthofsimulatedcorrosion. Second,theratiooftheamplitudeofthefirst
trailingechoandthebackechocorrelatedwithanincreaseinthelengthofsimulated
corrosion.
Theinvestigationofthetransitionofthesimulatedcorrosionconcludedthattheflawechois
detectableforabrupttransitionsof90downtoassmallas5. Theflawechoexperienceda
decreaseinamplitudebelowa80transitionanglebutwasstilldetectable. Twopeakswere
evidentat transitionanglesof27.5and45. Thesepeakscorrelatetoashearandlongitudinal
wavereflectiondirectlyacrosstherodfromthetransitionsurface.
Williamsallthreadtiebackrodswereinvestigatedincludingprojecteddetectablerodlength,
signalattenuationduetosurroundingmedia,andsimulatedcorrosionintiebackrods. The
signalsintiebackrodsshowedadistinctbackecho,withlowsignalamplitudefollowing,dueto
thedispersionofthewavefromthethreads. Sincethebackechodidnotreflectfromthe
threads,theamplitudewasnotaffected. Thesignalattenuationtestsrevealedthattherewas
nosignificantamplitudelossinthebackechoforsand,loosesoil,orcompactsoil. Aprojected
detectablerodlengthwasfoundtobe40feetwiththepulseechomethod. Finally,simulated
corrosioninWilliamstiebackrodsshowedthatlocationanddiameterofsimulatedcorrosion
weredetectableinthreadedrodswitha90anda45transitionangle.
Theworkpresentedinthisdissertationformsoriginalresearchthatcontributestothefollowing
fields:
1. SafetyofstructureswithinthefieldofCivilEngineering
2. AddingtothecurrentliteratureofNDTtesting
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
120/123
108
Thesecontributionsinclude:
1. Effectoftransitionsontheultrasonicsignal
2. Effectoflengthofcorrosionontheultrasonicsignal
3.
Effectofsoilontiebackrodsignalattenuation4. DetectionofsimulatedcorrosioninWilliamstiebackrods
Basedontheresearchpresented,thefollowingrecommendationsweremadeforfuture
research.
1. Investigatetheminimumdetectablecrosssectionlossin1.0in.diametertiebackrods.
Forexample,machinerodswith0.8125in.,0.875in,0.9375in.diameterofsimulated
corrosionandidentifythesmallestsimulatedcorrosionthatexhibitsaflawecho.
2. Investigatethedetectabilityofsimulatedcorrosioninlargerdiametertiebackrods. For
example,machinesimulatedcorrosionin2.0in.and3.0in.diameterWilliamsrods,and
identifythedetectablegeometries.
3. Investigatethedetectabilityofadditionalgeometriccharacteristicsofsimulated
corrosionontheultrasonicsignalforthepulseechomethod. Forexample:
machinesimulatedcorrosionwithavariationindiameterinthecorrodedregion,
insteadofuniformreduceddiameter.
machinenonconcentriclossofcrosssectioninsteelrods.
4. Investigatethedetectionofultrasonicsignalsinrodswithcurvaturetomimicrodsthat
havebentduringsettlement. Bendmultiplecommercialtiebackrodstovariousradii
andmonitortheultrasonicsignal.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
121/123
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
122/123
110
ReferencesCited:
ASTMStandardA108.(2007).StandardSpecificationforSteelBar,CarbonandAlloy,Cold
Finished,DOI:10.1520/A010807.WestConshohocken,PA:ASTMInternational.
ASTMStandardA29.(2005).StandardSpecificationforSteelBars,CarbonandAlloy,Hot
Wrought,GeneralRequirementsfor,DOI:10.1520/A0029_A0029M05.WestConshohocken,
PA:ASTMInternational.
ASTMStandardA615.(2008).StandardSpecificationforDeformedandPlainCarbonSteelBars
forConcreteReinforcement,DOI:10.1520/A0615_A0615M08B.WestConshohocken,PA:
ASTMInternational.
ASTMStandardD2216.(2005).StandardTestMethodsforLaboratoryDeterminationofWater
(Moisture)ContentofSoilandRockbyMass,DOI:10.1520/D221605.WestConshohocken,
PA:ASTMInternational.
ASTMStandardD422.(2007).StandardTestMethodforParticleSizeAnalysisofSoils,DOI:10.1520/D042263R07.WestConshohocken,PA:ASTMInternational.
ASTMStandardD4318.(2005).StandardTestMethodsforLiquidLimit,PlasticLimit,and
PlasticityIndexofSoils,DOI:10.1520/D431805.WestConshohocken,PA:ASTMInternational.
Beard,M.,Lowe,M.,&Cawley,P.(2001).InspectionofRockboltsusingGuidedUltrasonic
Waves.ReviewofProgressinQuantitativeNondestructive Evaluation,11561163.
Bray,D.E.,&Stanley,R.K.(1989).NondestructiveEvaluation.NewYork:CRCPress.
Davies,R.(1948).ACriticalStudyoftheHopkinsonPressureBar.Phil.Transactions,375457.
Esser,A.J.,&Dingeldein,J.E.(2007).FailureofTiebackWallAnchorsDuetoCorrosion.Geo
Denver2007,(pp.110).Denver.
Hudson,G.(1943).DispersionofElasticWavesinSolidCircularCylinders.PhysicsReview,46
51.
Kolsky,B.(1963).StressWavesinSolids.NewYork:DoverPublicationsInc.
Krautkramer,J.,&Krautkramer,H.(1990).UltrasonicTestingofMaterials.Berlin:Springer
Verlag.
Light,G.M.,&Joshi,N.R.(1987).UltrasonicWaveguideTechniqueforDetectionofSimulated
CorrosionWastages.NondestructiveTestingCommunications ,1327.
Main,L.G.(1988).VibrationsandWavesinPhysics.NewYork:CambridgeUniversityPress.
Niles,G.B.(1996).InSituMethodforInspectingAnchorRodsforSectionLossUsingthe
CylindricallyGuidedWaveTechnique.IEEETransactionsofPowerDelivery,16011605.
-
7/31/2019 ULTRASONIC DETECTION OF SIMULATED CORROSION IN 1 INCH DIAMETER STEEL TIEBACK RODS
123/123
Pochhammer,J.(1876).Aboutthereproductionspeedsofsmallvibrationsinaninfinite
isotropiccircularcylinder.JournalofPureandAppliedMath,324336.
Pollock,D.G.(1997).ReliabilityAssessmentofTimberConnectionsThroughUltrasonic
InspectionofBolts.TexasA&MUniversity.
USArmyCorpsofEngineers.(1994,March31).RetrievedJanuary18,2009,fromDesignof
SheetPileWalls:http://140.194.76.129/publications/engmanuals/em111022504/
WilliamsFormEngineeringCorp.(2008).RetrievedApril2,2009,fromTieRodInformation:
http://www.williamsform.com/